Jeff,
thank you very much for your help. Yes, Parameter 3 should be 8 and I need the calculated maximum on 10:00 pm on the same day to 10:00 am on the next day.
The new Fortran code is great! I have found an other acceptable solution: I can use the Input value recall some hours later and compare it with the current value in the Equation mode. So I get always the highest value from the last day. But this might be not acceptable for all technical problems, so your Fortran code is much more comfortable.
kindly regards,
Henrik
Henrik,
I am confused by your e-mail. Are you saying that you would like the
periodic integrator to calculate the maximum value of an input from 11:00
am to 7:00 pm and then use this calculated output as an input to another
component during the hours of 10:00 pm to 10:00 am the next day? (Parameter
3 should be 8 by the way)
Assuming that this is your intent, I ran a simple input file to test what
TYPE 55 is doing. You are correct in that the periodic integrator is
resetting the outputs at midnight - or 24 hours from the start of the
simulation as you have specified in your parameter list. After discussing
this with several of my colleagues, we have decided that the best thing is
to change type 55 to do as you suggest - reset the values every 24 hours
after the start of the summary period - and not every 24 hours after the
start time of the simulation. While the old method wasn't wrong - the new
change that we have made will make the program a little more flexible.....
If you have a FORTRAN compiler the OLD and NEW FORTRAN code is supplied
below. Otherwise contact your TRNSYS distributor in a few days for the
latest source code.
With kindest regards,
Jeff
(Type 55 author)
OLD CODE
C SET THE INITIAL VALUE OF THE RESET TIME
IF(MONTH3(I)) THEN
RESET(I)=MONTH(KEEP(I))
NEWVAL(I)=RESET(I)
ELSE
CNB CHECK IF PERIOD IS LONGER THAN A DAY
IF((TON(I)+LENGTH(I)).GT.RESET(I)) THEN
NEWVAL(I)=TON(I)+RESET(I)
ELSE
NEWVAL(I)=TIME0+RESET(I)
ENDIF
ENDIF
NEW CODE
C SET THE INITIAL VALUE OF THE RESET TIME
IF(MONTH3(I)) THEN
RESET(I)=MONTH(KEEP(I))
NEWVAL(I)=RESET(I)
ELSE
NEWVAL(I)=TON(I)+RESET(I)
ENDIF
*********************************************************************************