dear Prapapong Vangtook,
QALTL <> 0 during daytime
makes sense, since you operate your active layer during nite time
only
QCOMI < 0
Since QCOMI
is the energy from inside surface incl. conv to the air and I-wave
radiation to other surfaces; as long as this surface absorbs heat
-> QCOMI <0 is correct. I assume your
active wall has enough thermal storage. Why shouldn't this make sense?
Hope this helps.
regards,
matthias rudolph
Dear TRNSYS users,
I got some problem about output of a active
layer. A simulation is run by case of running active layer in night time
and stop in day time. The results QALTL (total energy input by fluid+gains
of active layers to zone) is zero in daytime but QCOMI (energy from inside
surface incl, conv to the air and I-wave radiation to other surfaces) is
still get minus value (-300 kJ/hr). otherwise in night time, QALTL is 1038
kJ/hr and QCOMI is -350 kJ/hr too. It can not possible because on day time
the room air is vary hot (35 C) and also vary high of solar radiation on
the external wall. Please explain this happening.
Best
Regards, Prapapong Vangtook
|