Dear Howard,
Type 4 is easier to use than Type 60 but it does not allow you to
simulate internal heat exchangers. If you don't have internal heat
exchangers or if you can neglect them, I would recommend that you use
Type 4. On the other hand, Type 60 uses its own internal time step. Type
4 uses TRNSYS time step, which may lead to numerical instabilities in
some cases, e.g. if you have high flowrates to/from the tank and a large
number of nodes (usually, the problem is easily fixed by reducing the
TRNSYS time step).
Regarding the number of nodes, several studies have shown that using a
relatively small number of nodes (<=10) gives a satisfactory accuracy
for yearly simulation of solar systems. The problem is of course
different if you want to simulate a particular tank design accurately,
especially if you are interested in short-term/transient behavior. You
could start using a small number of nodes and then increase it
progressively. You can then decide how many nodes you need to obtain a
good accuracy in your particular case. Of course, this assumes that the
real tank is actually stratified.
The current version of Type66 is restricted to one instance per
simulation. However, the EES solver can cope with a large number of
equations so you can group different components in the same EES file.
Regards,
Michaël Kummert
Howard wrote:
Dear all,
Currently I am trying to model a hot water storage tank for storing
water heated by a heat pump. There are two similar models, the Type 4
and Type
60 in the TRNSYS and I would like to know:
- Any general guidelines to decide which Type of storage tank should
be used?
- How do we define the number of stratification? Aren't the
stratification is a natural phenomena?
On the other hand, I tried to write my own component in EES (such as
the compressors, condensers) and would like to add them into the
Trnsys project by Type66 module.
However, plenty of error popped up when I started the simulation if
two or more Type66 module is used. I sorted out there may be some
problem with the data transfer through CLIPBOARD but I cannot resolve
it indeed. Does anyone have similar experience before which can share?
Regrads,
Howard But
The University of Hong Kong
--
_________________________________________________
Michaël Kummert
Solar Energy Laboratory - University of Wisconsin-Madison
1303 Engr Res Bldg, 1500 Engineering Drive
Madison, WI 53706
Tel: +1 (608) 263-1589
Fax: +1 (608) 262-8464
E-mail: kummert@engr.wisc.edu
SEL Web Site: http://sel.me.wisc.edu
TRNSYS Web Site: http://sel.me.wisc.edu/trnsys