[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: WALL TIMEBASE and timesteps
- Date: Wed, 10 Dec 2003 09:25:44 -0600
- From: Michaël Kummert <kummert@xxxxxxxxxxxxx>
- Subject: Re: WALL TIMEBASE and timesteps
on 2003-12-10 07:56, Tomas Persson wrote:
Hi!
I have also had some problems with increasing temperatures up to several
hundred Celcius inside type 56 (self-heating!?). It looks like if there
is a large deck-file with a hundred different components, type 56 should
be placed in the beginning of the deck-file, to avoid "self-heating"
I have also had self-heating, when I used type 2 (on-off controler) with
the "new control strategy". Check that you don´t use the "new control
strategy" if you have the on-off controler in your deck-file.
The "Type2 and New Control Strategy" problem might be an explanation of
the problem: in TRNSYS releases older than 15.3.00, there is no check
that the mode used for Type 2 corresponds to the selected solver. And it
is true that using a solver and a Type 2 mode that do not match each
other can lead to very strange results (including inexplicable
temperature increase of Type 56).
TRNSYS 15.3.00 now gives an error message and stops the simulation.
Just to make sure there is no misunderstanding, Type 2 works fine with
both solvers, you just have to make sure you use the corresponding mode.
Kind regards,
Michaël Kummert
--
_________________________________________________________
Michaël Kummert
Solar Energy Laboratory - University of Wisconsin-Madison
1303 Engr Res Bldg, 1500 Engineering Drive
Madison, WI 53706
Tel: +1 (608) 263-1589
Fax: +1 (608) 262-8464
E-mail: kummert@engr.wisc.edu
SEL Web Site: http://sel.me.wisc.edu
TRNSYS Web Site: http://sel.me.wisc.edu/trnsys