Dear Stefano,
Type 9 can read data with any time step that is acceptable for TRNSYS.
TRNSYS 15 accepts time steps down to 0.001 h (3.6 sec). The time step must
satisfy the following requirements:
- If it is less than 0.02, it must be the
reciprocal of an integer smaller than 1000.
- If it is greater than 0.02, it must be the ratio
of two integers (with a denominator <= 50)
Note that the current TRNSYS release (15.3.00) rounds the time step to the
nearest value which matches those criteria if necessary. In this case, a
warning is issued.
You example, 10 sec, is 1/360 hour so it is OK (it would not be rounded).
Here are a few examples of time steps and what TRNSYS would do with them:
dt[sec] | dt [h] | rounded to (fraction)
---------------------------------------------
1.00 | 0.00027778 | 0.00100000 (1/1000)
anything < 3.6 sec | 0.00100000 (1/1000)
3.60 | 0.00100000 | Not rounded (1/1000)
10.00 | 0.00277778 | Not rounded (1/360)
30.00 | 0.00833333 | Not rounded (1/120)
60.00 | 0.01666667 | Not rounded (1/60)
77.00 | 0.02138889 | 0.02127660 (1/47)
120.00 | 0.03333333 | Not rounded (1/30)
145.00 | 0.04027778 | 0.04000000 (1/25)
300.00 | 0.08333333 | Not rounded (1/12)
I hope this helps,
Michaël Kummert
_________________________________________________________
Michaël Kummert
Solar Energy Laboratory - University of Wisconsin-Madison
1303 Engr Res Bldg, 1500 Engineering Drive
Madison, WI 53706
Tel: +1 (608) 263-1589
Fax: +1 (608) 262-8464
E-mail: kummert@engr.wisc.edu
SEL Web Site: http://sel.me.wisc.edu
TRNSYS Web Site: http://sel.me.wisc.edu/trnsys
> -----Original Message-----
> From: owner-trnsys@relay.doit.wisc.edu
> [mailto:owner-trnsys@relay.doit.wisc.edu] On Behalf Of
> Stefano.Esposto@uniroma1.it
> Sent: Thursday, May 22, 2003 08:48
> To: trnsys@relay.doit.wisc.edu
> Subject: Type 9
>
>
> Dear TRNSYS users,
> I've a question about the data readable by the type 9. I've
> seen that it's possible to read for a trnsys simulation
> weather data recorded hourly o daily.Is it possible to read
> datas recorded with lower interval of time (for example
> minutes or seconds)?. I'm asking this because I've the
> possibility to have data recorded by our weather station each
> second, and I would like to make simulation in ISIBAT using
> these datas for short simulation (3-4 hours with a simulation
> time step of 10 seconds). Thank you
>
> Regards
>
> Stefano Esposto
>